Question
A single-phase load is connected between R and Y terminals of a 220 V, symmetrical, 3-phase, 4 wire systems with phase sequence RYB. A watt-meter is connected in the system. The watt-meter will read (pf = 0.8 lagging)?
Answer: Option B
Answer: (b).– 168 W
Was this answer helpful ?
Answer: (b).– 168 W
Was this answer helpful ?
Submit Solution