Sail E0 Webinar
Question
A single pass shell and tube heat exchanger, consisting of a bundle of 100 tubes (inner diameter 25 mm and thickness 2 mm) is used for heating 28 kg/s of water from 25 degree Celsius to 75 degree Celsius with the help of a steam condensing at atmospheric pressure on the shell side with condensing heat transfer coefficient 5000 W/m² degree. Make calculation for overall heat transfer coefficient based on the inner area. Take fouling factor on the water side to be 0.002 m² degree/W per tube and neglect effect of fouling factor on the shell side and thermal resistance of the tube wallA Single Pass Shell And Tube Heat Exchanger, Consisting Of A...
Options:
A .  647.46 W/m² degree
B .  747.46 W/m² degree
C .  847.46 W/m² degree
D .  947.46 W/m² degree
Answer: Option C
Answer: (c).847.46 W/m² degree