Question
The overall heat transfer co-efficient for a shell and tube heat exchanger for clean surfaces is U0 = 400 W/m².K. The fouling factor after one year of operation is found to be hd0 = 2000 W/m².K. The overall heat transfer co-efficient at this time is
Answer: Option C
Answer: (c).333W/m².K
Was this answer helpful ?
Answer: (c).333W/m².K